Sean

Hello,

I have compiled the program with success. I then launched the Virtual PLC CPU, and when I selected to connect with the PLC a warning message came up stating "Current Virtual PLC CPU program is different from EasyPLC Editor Project !!!!". Attached please find this warning message.
I then select OK and try to Transfer program to PLC. When I clik the transfer button nothing happens and an error in the virtual plc occurs (see attached). The progress bar of the "Uploading PLC program ..." does not progress when continue is selected, and the program is not transferred to the PLC.

I appreciate your help on this one. Attached find also the program.

Thanks a lot and kind regards,
Sean

[attachment deleted by admin]

EasyPLC_Master

Hello Sean;

The message "Current Virtual PLC CPU program is different from EasyPLC Editor Project !!!!" means that the PLC recognizes that the proyect you are transfering from the Editor is different from the one that is loaded in the PLC, only is an alarm but not is an error.

About the second problem you report is due your antivirus software or firewall system is blocking the TCP connection between the EasyPLC Editor and the Virtual PLC, then is not possible to transfer the program, in order to solve you must to configure the program access as administrator and must add an exception to your antivirus/firewall.

More detailed instructions are posted here:

http://nirtec.com/forum/index.php?topic=248.0