General Category => Machines Simulator => Troubleshooting => Topic started by: pitowilson on April 24, 2024, 02:22:10 PM

Title: Driver not connected
Post by: pitowilson on April 24, 2024, 02:22:10 PM
Hello,
Suddenly I have a problem with connection between TIA (v16) and machine simulator. Everything worked, I didn't change anything on PC or anywhere and it's not working anymore. I have tried exchange i/o between TIA and Easy PLC - succesful. I am currently running MS version 3.2, but I have also tried it with the lastest version of MS - not working. There is always sign Driver not connected.
Does anybody know where could be the issue ?
Thanks in advance,
Miroslav
Title: Re: Driver not connected
Post by: EasyPLC_Master on April 24, 2024, 07:30:10 PM
Hi Miroslav!

We have tested the drivers with MS v.4 and all are working properly.
Can you send us more information about the error? a screenshot of the MS Siemens Driver configuration will help.
Title: Re: Driver not connected
Post by: pitowilson on April 25, 2024, 08:54:06 AM
Hello,
I'm sending you printscreens of configuration and fail
Title: Re: Driver not connected
Post by: EasyPLC_Master on April 27, 2024, 08:08:01 PM
I saw you have DB's configured, then first try this:

1. Remove DB's reading, set DB for Analog I/O to 0 and DB length to 0

Now you should connect.

The second test is that you must be sure you have the same DBs number and length used in TIA PORTAL and declared in the driver as analog I/O declared in Machines Simulator Editor otherwise do not connect.