Nirtec Studio Forum

General Category => Machines Simulator => Topic started by: toku1991 on February 20, 2022, 01:00:07 AM

Title: keep getting errors
Post by: toku1991 on February 20, 2022, 01:00:07 AM
Hey people

i try to connect machine simulator with tiaportal
and if i open nettoplcsim i keep getting the error message port 102 not availeble and if i stop the running process it will not find any plc's

Title: Re: keep getting errors
Post by: EasyPLC_Master on February 20, 2022, 06:42:14 PM
Hi!

In order to work properly, you need to launch nettoplcsim first than Siemens PLCSIM, otherwise, the problem you indicate will occur.
In the following video made by one user (in Spanish) is explined how to make the connections with a 1500 CPU step by step: https://youtu.be/Gs0tNGzNWxQ (https://youtu.be/Gs0tNGzNWxQ)

Also, please note that a special configuration must be done in TIA PORTAL:

DB -> Uncheck Optimized block access, by default it's checked
Protection -> Select the CPU project in the left pane and press Alt-Enter (or in the contextual menu select "Properties..."). In the item Protection, select "Full access" and Check "Permit access with PUT/GET ...."

Here you can download the EasyPLC/Machines Simulator Driver for Siemens PLC Instructions document -> https://drive.google.com/file/d/16e0MtSwBPOD_YGORrYeTlQ6rbkgigSmS/view?usp=sharing (https://drive.google.com/file/d/16e0MtSwBPOD_YGORrYeTlQ6rbkgigSmS/view?usp=sharing)
Title: Re: keep getting errors
Post by: toku1991 on February 21, 2022, 03:05:30 PM
Thanks its working now  ;D