I have a problem to connect the mx opc server 6.10 with machines simulator.
I can communicate between the mx and the io configurator but in the simulator itself there is no response to io even if opc connected
Any ideas?
Thanks,
Chen
Hi!
Please inform:
- EasyPLC version
- Machines Simulator version
Have you test to connect EasyPLC with mx opc server 6.10? works ok then? with Machines Simulator works the communication with the IO_Driver_Configurator.exe utility?
Thank you for the quick reply!
EasyPLC Version - 5.9.2.0
Machines Simulator 3 - 1.0.0.0
I did a test with EasyPLC, indeed, it responds.
Also the IO_Driver_Configurator responds well on test mode.
The thing is that when I save the settings in the IO_Driver_Configurator and connects to the machine in the simulator itself
same as this video: https://www.youtube.com/watch?v=d1F4y92g6AQ
even with the "Connected!" label at the left-bottom, there is no response from the IO's
Sorry, I looked again at the sent USB instead of the properties of the files and the versions are-
EasyPLC Version - 5.9.3.B
Machines Simulator 3.3.1.B
???
OK, I will contact you in order to check your system!
To close this thread, the problems found have been corrected in the Machines Simulator ver 3.3.1.C