I have installed easyplc/machine simulator in my laptop. I have softlogix on a virtualbox.
Does anyone have experience setting it up to receive data in opc to easyPLC?
Please see the following examples:
https://youtu.be/d1F4y92g6AQ (https://youtu.be/d1F4y92g6AQ)
https://www.youtube.com/watch?time_continue=3&v=c9RfjeupVfc (https://www.youtube.com/watch?time_continue=3&v=c9RfjeupVfc)
https://www.youtube.com/watch?v=JPE3lQjmgJ8 (https://www.youtube.com/watch?v=JPE3lQjmgJ8)
https://www.youtube.com/watch?v=Y8o-pcs2WW8 (https://www.youtube.com/watch?v=Y8o-pcs2WW8)
https://www.youtube.com/watch?v=1Mnn4o7oVXY (https://www.youtube.com/watch?v=1Mnn4o7oVXY)
https://www.youtube.com/watch?v=h1jYQ98IuH8 (https://www.youtube.com/watch?v=h1jYQ98IuH8)
I ended up doing everything in my laptop. I have RSLogix5000, RSLinx Classic, and SoftLogix5800.
After I download my small program with two controller tags, and two program tags.
I can then browse tags with Matrikon OPC Explorer.
When I try to setup opc in easyplc I get the following error, even when the RSLinx OPC Server is online:
Driver Not Ready.
Message: OPC Client could not connect to: "RSLinx OPC Server"
Not sure what I am doing wrong, I follow the video on youtube for rslogix5000 and doesn't seem like there's anything to it other than adding tags to inputs and outputs.
My issue is resolved after reading the opc guide and reading this post.
http://nirtec.com/forum/index.php?topic=303.0
http://nirtec.com/forum/index.php?topic=318.0 <- opc guide for RSLinx OPC Server
OK fredz0003, thank you for sharing your experience!